SH5107: A Laboratory Fume Hood, Hood Opening Area A = 40 ft2 (3.72 m2): Industrial Ventilation Assignment, NUS, Singapore

University National University of Singapore (NUS)
Subject SH5107: Industrial Ventilation

Assignment 4 – Specific Hood

Question 1

A laboratory fume hood, hood opening area A = 40 ft2 (3.72 m2), face velocity = 100 fpm (0.5 m/s), entry loss factor f = 0.5. Assume STP.

  1. Determine the volume flow rate required.
  2. Size the duct to give a duct velocity of nearest 2,000 fpm (10 m/s) and round off the diameter to a whole number in inches or cm.
  3. Determine the hood static pressure (SPh).

Question 2

  1. A canopy hood is being used on an open-surface tank, which is not located near any walls. The hood is located 1.2 m (4 feet) above the top of the tank. If the tank is 1.8 m (6 feet) long and 0.9 m (3 feet) wide and the contents are at room temperature, what airflow through the hood is required? Assume a control velocity of 0.75 m/s (150 ft/min).
  2. If a lateral slot hood is used to capture the vapor evaporated from the same open-surface tank with the same control velocity of 0.75 m3/s/m2 (150 ft3/min/ft2) of tank area. What airflow through the hood is required?

Stuck with a lot of homework assignments and feeling stressed ? Take professional academic assistance & Get 100% Plagiarism free papers

Question 3

  1. A high canopy hood is to be placed 5 ft (1.5 m) above a crucible furnace 3 ft (0.9 m) in diameter, what will be the diameter Dc of the rising hot air column at the hood face?
  2. In question A, if the furnace temperature is 932°F (500°C) and the ambient temperature is 86°F (30°C), determine the velocity of the air column at the hood face (Vf) and the total exhaust airflow rate Qt through the hood.

Question 4

A low canopy hood is to be installed to capture the emissions during fluxing and slagging of brass in a 1.50 m diameter ladle. The metal temperature during this operation will not exceed 800°C. The hood will be located 1.00 m above the metal surface. The ambient air temperature is 35°C. Determine the exhaust rate required. (Note: diameter of hood = diameter of source + 0.3 m)

Question 5

A die-casting machine is with a rectangular holding pot 0.50 m wide by 1.00 m long for molten metal. A low canopy hood is to be provided 0.80 m above the pot. The metal temperature is 440°C. The ambient air temperature is 30°C. Determine the exhaust rate required. (Note: length or width of hood = length or width of source + 0.3 m)

Get Help By Expert

If you are stuck with the (SH5107) industrial ventilation assignment writing tasks then don't worry. We are at your services 24/7. Our nursing assignment experts will throw away all your problems and worries related to industrial ventilation assignments by providing you with the finest healthcare management assignment solutions with assured great results.

Answer

Looking for Plagiarism free Answers for your college/ university Assignments.

Ask Your Homework Today!

We have over 1000 academic writers ready and waiting to help you achieve academic success